Outdoor Romex?

I'm replacing an outdoor lamp post with a new one. I noticed the Romex (cable?) coming into the lamp has a bad break on it down to one of the wires. I've always been able told not to tape this kind of thing up, but replace that part of the cable. I've worked with Romex inside the house, but not outside. Is there such a thing as outdoor Romex? Or is it called something else for wiring that has a white, black and ground wires but can be used outside that it can be buried in the ground? The existing wire inside the lamp post has no conduit on it.
#2
Old 08-26-2015, 12:07 AM
Charter Member
Join Date: Jun 1999
Location: Milwaukee, WI
Posts: 26,539
Quote:
Originally Posted by edwardcoast View Post
I'm replacing an outdoor lamp post with a new one. I noticed the Romex (cable?) coming into the lamp has a bad break on it down to one of the wires. I've always been able told not to tape this kind of thing up, but replace that part of the cable. I've worked with Romex inside the house, but not outside. Is there such a thing as outdoor Romex? Or is it called something else for wiring that has a white, black and ground wires but can be used outside that it can be buried in the ground? The existing wire inside the lamp post has no conduit on it.
They make Romex specifically for underground applications. IIRC, it'll say UG on it. It's heavier than the normal stuff and harder to work with. I wouldn't attempt to splice a new section, but just replace the entire run if that's feasible. But I don't know how to make splices underground.

Home Depot/Lowes will have it, it's usually gray instead of yellow or white and it'll say it's rated for underground/burial.

Last edited by Joey P; 08-26-2015 at 12:10 AM.
#3
Old 08-26-2015, 12:51 AM
Guest
Join Date: Apr 2010
Posts: 11,921
Type UF-B (Underground Feeder-Branch). Looks similar to Romex, good bit more expensive, used just the same except it is much trickier to strip. You may want to practice cutting away the solid-cast cable body (without nicking the individual conductor insulation) with your razor knife, before trying your actual installation.
#4
Old 08-26-2015, 12:52 AM
Guest
Join Date: Jan 2014
Posts: 958
Quote:
Originally Posted by Joey P View Post
They make Romex specifically for underground applications. IIRC, it'll say UG on it. It's heavier than the normal stuff and harder to work with. I wouldn't attempt to splice a new section, but just replace the entire run if that's feasible. But I don't know how to make splices underground.

Home Depot/Lowes will have it, it's usually gray instead of yellow or white and it'll say it's rated for underground/burial.
Thanks for the reply.

This is for a lamp post that can support three 100 Watt bulbs which is 110v or 120v and is connected to a 15 Amp which is shared with lights and stuff on the same circuit. Does that mean I should use a 14/2 plus ground UG Romex? Or because it's outside use something more heavy like 12/2? And I can't tell what the existing Romex is, because it's coming out of the ground and any printing on it is either rubbed off or too hard to read.

Last edited by edwardcoast; 08-26-2015 at 12:54 AM.
#5
Old 08-26-2015, 12:58 AM
Guest
Join Date: Jan 2014
Posts: 958
Quote:
Originally Posted by Peremensoe View Post
Type UF-B (Underground Feeder-Branch). Looks similar to Romex, good bit more expensive, used just the same except it is much trickier to strip. You may want to practice cutting away the solid-cast cable body (without nicking the individual conductor insulation) with your razor knife, before trying your actual installation.
Thanks for the suggestion. When I have seen experienced electricians work, they make it look too easy and work very fast. I only need something like 4-5 feet of Romex for this, but I will purchase more feet so I can practice with it.
#6
Old 08-26-2015, 07:26 AM
Guest
Join Date: Sep 2014
Location: Southeast
Posts: 641
Not the right answer per code but if you're simply wanting to cover the break, my local NAPA Auto Parts carries large diameter, glue lined heat shrink tubing. They use it on custom battery and welding cables. A 4" long piece would bond to the existing Romex and seal the break.
#7
Old 08-26-2015, 10:37 AM
Charter Member
Join Date: Sep 2003
Location: Southeast Florida USA
Posts: 20,219
Nefario: Is this stuff a closed tube or is it a self-adhesive sheet you wrap around your cable? Said another way, can it be installed without disconnecting the cable at either end?

I'm asking not for the OP, but for a different but similar problem I've got where I'd like to heat shrink over a damaged section that's impossible to disconnect at either end.
#8
Old 08-26-2015, 11:24 AM
Charter Member
Join Date: Jun 2000
Location: St. Louis, MO 50mi. West
Posts: 4,419
They do make splice kits for underground cable. I've never used one but have seen them in the store. Two or three splice sleeves with screw logs and a bunch of heat shrink tubing. The outer piece of heat shrink is adhesive filled so the whole thing is water proof.

http://m.delcity.net/store/Undergrou...6vcaAkGr8P8HAQ

Here's one example.
__________________
GaryM
#9
Old 08-26-2015, 12:04 PM
Guest
Join Date: Dec 2009
Location: State of Jefferson
Posts: 7,510
Underground is the same as underwater, I'd be suspicious of a product designed for use on cars. I've seen underground cables sliced through and spliced together again. These 'normal' connections are encapsulated with epoxy, gallons of the stuff. Like a big softball sized chunk of cured epoxy glue around each wire nut. This should last a very long time submerged.

I'd replace the cable myself, and I'd make sure to bury it deep, couple feet or more. A 15 amp breaker will carry 14 gauge wire safely, I do believe, but that's a good question to ask about.

Last edited by watchwolf49; 08-26-2015 at 12:04 PM.
#10
Old 08-26-2015, 12:06 PM
Guest
Join Date: Sep 2014
Location: Southeast
Posts: 641
Quote:
Originally Posted by LSLGuy View Post
Nefario: Is this stuff a closed tube or is it a self-adhesive sheet you wrap around your cable? Said another way, can it be installed without disconnecting the cable at either end?
The stuff I found at NAPA was closed tubing that I used to repair a used welding handpiece that was broken.

BUT - there used to be self-healing silicone? tape that could be wrapped around an intact wire and forms a solid rubbery mass. I didn't want to suggest this and get into a debate about whether this would be weatherproof. No connection to me....

http://ebay.com/itm/Wire-Tie-Sel...item3f3fd3b36f

Or try McMaster - Carr.

Last edited by Nefario; 08-26-2015 at 12:10 PM.
#11
Old 08-26-2015, 12:12 PM
Charter Member
Join Date: Sep 2003
Location: Southeast Florida USA
Posts: 20,219
Thanks. My application is low voltage signaling, so no danger.
#12
Old 08-27-2015, 09:45 AM
Guest
Join Date: Jan 2014
Posts: 958
Quote:
Originally Posted by Peremensoe View Post
Type UF-B (Underground Feeder-Branch). Looks similar to Romex, good bit more expensive, used just the same except it is much trickier to strip. You may want to practice cutting away the solid-cast cable body (without nicking the individual conductor insulation) with your razor knife, before trying your actual installation.
Just wanted to post an update and say thanks again! I bought the UF-B and you weren't kidding, that is very hard to strip compared to indoor Romex. I'm glad I got extra feet to make sure I had enough to practice with. I finished the project and got the new lamp post installed.

Tip to anyone else working on outdoor lighting, start the project as early in the day as you can so you don't end up trying to finish it while it's getting dark. :-)
#13
Old 08-27-2015, 06:11 PM
Guest
Join Date: Mar 2003
Location: Minneapolis, MN
Posts: 13,513
Quote:
Originally Posted by GaryM View Post
They do make splice kits for underground cable. I've never used one but have seen them in the store. Two or three splice sleeves with screw logs and a bunch of heat shrink tubing. The outer piece of heat shrink is adhesive filled so the whole thing is water proof.
Yes, but those are pretty expensive. Usually more than the 6 feet of UF that the OP needs.
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is Off
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 11:53 AM.

Copyright © 2017
Best Topics: bobtails ring mushrooms diarrhea long run generators average head dimensions lockpicking games most maneuverable bird cracker jack jingle dnr wire tap quinceanera gift etiquette wound vac pictures pickles on pizza wifes stocking como tally vous navel diagram edited to add penis shedding brown prionid beetle do spiders poop lessons learned synonym repairing guitar neck sweating during naps grocery store scales radio bandwidth niggertoe nuts vegetable multivitamin lay pipe barfing smilie pants unzipped neon repair cost think though nuisance dust what was the original name for a jack in a standard deck of poker cards? can autozone test alternator how to cite something someone said blair witch 2 hidden messages can you use dog shampoo on human hair is jerry springer real? what does mint smell like how to blend food without a blender how much is a gold quarter worth from 2000 who played adam on bonanza general anesthesia wisdom teeth experience tony robbins height weight what does durka durka mean three dots in a row meaning tip hotel shuttle driver why do i have to force myself to eat how hard is swedish to learn potty training australian shepherd puppies how long can cooked shrimp sit out 2004 saturn vue check engine light bands like king crimson rap songs with the word baby do you tip a tow truck driver can you use a drain auger on a toilet where can i go to cash a check without id carla gugino and rachel weisz teddy boy jacket pattern a group of pill pushers wheel of fortune what smells like skunk but isn't skunk chinese restaurant that cooks in front of you does grammar include punctuation who killed lester at the end of american beauty speed limit signs on expressway exit ramps are generally colored __________ .